Our forum has been available for many years. In September 2014 we decided to switch it to read-only mode. Month after month we saw less posts with questions and answers from real people and more spam posts. We were spending more and more resources cleaning the spam until there were less them 1 legitimate message per 100 spam posts. Then we decided it's time to stop.

All the posts in the forum will be available and searchable. We understand there are a lot of useful information and we aren't going to remove anything. As for the new questions, you can always ask them on convert-me.com FaceBook page

Thank you for being with us and sorry for any inconveniences this could caused.

Voltage Drop

Mon Apr 12, 2004 8:12 pm

What size aluminum conductor should I use? Service line for a poultry house, 120/240 volt service, 155' from trasformer pole to load site. Estimated load is 190 amps and I can only have a 1.5% voltage drop.

Re: Voltage Drop

Tue Apr 13, 2004 2:19 am

jcash wrote:What size aluminum conductor should I use? Service line for a poultry house, 120/240 volt service, 155' from trasformer pole to load site. Estimated load is 190 amps and I can only have a 1.5% voltage drop.
The answer, of course, is that you shouldn't use aluminum at all.

The answer is 350 kCmil wire. tough to find. You'll want to use 4/0 copper in real life.

Check out http://www.electrician.com/vd_calculator.html for a handy voltage drop calculator.

http://www.powerstream.com/Wire_Size.htm has a good reference for finding resistivity of copper wire. all you'll need to remember is that aluminum wire has a k 1.64 times that of copper, and you should be able to convert.

cable size comparison

Wed Mar 02, 2005 6:48 am

Knight wrote:
jcash wrote:What size aluminum conductor should I use? Service line for a poultry house, 120/240 volt service, 155' from trasformer pole to load site. Estimated load is 190 amps and I can only have a 1.5% voltage drop.
The answer, of course, is that you shouldn't use aluminum at all.

The answer is 350 kCmil wire. tough to find. You'll want to use 4/0 copper in real life.

Check out http://www.electrician.com/vd_calculator.html for a handy voltage drop calculator.

http://www.powerstream.com/Wire_Size.htm has a good reference for finding resistivity of copper wire. all you'll need to remember is that aluminum wire has a k 1.64 times that of copper, and you should be able to convert.
I am using 4/0 welding cable; what is the equilivent in "HCM" size?

Re: cable size comparison

Thu Mar 03, 2005 12:06 am

peter upton wrote:I am using 4/0 welding cable; what is the equilivent in "HCM" size?
I'm not sure what "HCM size" is. AWM 4/0 wire (American Wire Gauge) is 120 mm for metric standard.